You'd need to have one hell of a big system to overload a single 15A circuit. That's almost 2000W. Here's a conservative list of a beefy sample system:
800W - nice MH lighting system
200W - Heaters
100W - Sump return pump
50W - Skimmer pump
100W - Misc. powerheads and such
--------
1250W - Plenty of room on a single circuit
Not so fast.
Those numbers you stated are the steady-state power consumption. What causes the breaker to trip is the immediate current spike when power returns right after the outage. The coils in the ballasts and the motors in the pumps draw a lot more current during the startup than in the steadystate.
It would be wise to distribute lightings and pumps to different breakers if you can.
And it is perfectly fine to use heavy-duty extension cord for the lights. As long as it is equivalent or more capacity than the wire between the breaker and the outlet in the wall.