Rob, also keep in mind that the float switches have a maximum current rating - which is consumed by the wattage/voltage combinations of all of the equipment running off of that switch. If I remember correctly, most of the float switches I was looking at were rated for 0.7A or so - which is approximately 80 watts at 120V (conservatively). It doesn't take much to use up all of that power. If you exceed the current rating of the switch, it could melt or (possibly worse) have the contacts welded shut - making it no longer a switch (= FLOOD).
(I also agree that stray voltage is still a concern... and although you have heaters and pumps in the sump, they are well designed to handle and isolate the 120V... the float switches are not, IMO.)
Also, I believe that you were looking for a source for latching relays that weren't 30$. If you review my original post in this thread, you will find a link to the latching relay I used for my ATO. I got it from DigiKey.COM and it was cheap - I think 5 or 7$.
Hope this helps...
Jeff.
(I also agree that stray voltage is still a concern... and although you have heaters and pumps in the sump, they are well designed to handle and isolate the 120V... the float switches are not, IMO.)
Also, I believe that you were looking for a source for latching relays that weren't 30$. If you review my original post in this thread, you will find a link to the latching relay I used for my ATO. I got it from DigiKey.COM and it was cheap - I think 5 or 7$.
Hope this helps...
Jeff.